View Full Version : Gas pipe support code requirements


khe
04-14-2008, 12:27 PM
I noticed that my 1" gas pipe is not supported where it runs parallel to the floor joists. I plan on installing some supports but need to know the support interval I should use.

Thanks!

ToUtahNow
04-14-2008, 12:48 PM
I noticed that my 1" gas pipe is not supported where it runs parallel to the floor joists. I plan on installing some supports but need to know the support interval I should use.

Thanks!

12' Horizontal - 15' Vertical

Mark

OkieBill
04-14-2008, 06:23 PM
Michigan uses the International code series.

I would use the most stringent requirement to be on the safe side.

International Fuel gas code 2006- section 415 Table 415.1 states:

" Steel pipe 3/4 or 1 inch shall have spacing of supports @ 8 foot "



:thumbup2:

ToUtahNow
04-14-2008, 06:35 PM
I stand corrected as I referred to the IPC not the IFGC. That's the problem with the ICC and their Codes. Why would the Plumbing and the Fuel Gas Code contradict each other on pipe support. Perhaps that is why most of the West stuck with the Uniform Codes.

Mark

OkieBill
04-14-2008, 06:50 PM
I agree with you ToUtahnow, International is a pain!

khe
04-14-2008, 08:18 PM
Thanks for the information. I'll pick up some supports and install them at 8 foot intervals.

mtnman1100
04-15-2008, 09:38 PM
As many as you want. Go crazy:D

khe
04-16-2008, 11:45 AM
It was about 23 feet that was unsupported so I added three additional supports. It is now supported to code and that's good enough for me.:D

djrenek1
05-03-2008, 12:32 PM
i believe upc code is 6' on horizontal 1"

ToUtahNow
05-03-2008, 12:47 PM
i believe upc code is 6' on horizontal 1"

Under the UPC 6' is for 1/2" and 3/4' but it's 8' for 1".

Mark