2000 model Tempstar 10-ton RTU gas pack. Refrigeration system is 2 staged 5 ton systems. 1 stage uses the top half of the condensor coil and 2nd stage uses the bottom half. Theres 2 condensor fan motors which are both running at the same speed all the time.
The problem is 2nd stage cooling has high head pressure and cycles off the HPS. 1st stage pressures were 75 and 300. 2nd stage pressures will climb slowly and within a few minutes the high side climbs to 400 and the HPS will kick the 2nd stage off. The suction climbs to about 85.
The condensor coil is spotless, now. Before I foam-brited it the 2nd stage would cycle after about 20 seconds of runtime. After the cleaning, the 2nd stage would run for about 2 minutes.
I recovered 1 pound of refrigerant yesterday out of the 2nd stage yesterday, just as a temporary fix to get the head pressure down so they could have the 2nd stage running even if it is a limited capacity. Its been in the 90's and this unit is in a bar. I shut the unit down for an hour yesterday to clean the coil and they about ran me off. I got the head pressure down to about 360 steady and the suction dropped to about 70.
My next step is to recover everything out of the 2nd stage and weigh the 9lbs 6ounces back in. This would eliminate the possibility of being overcharged. I would have recovered everything out of the 2nd stage yesterday but all my cylinders were full. But, I'm real sure its not overcharged. I dont think anyone but me has worked on it. And, if someone else did have their gauges on it, I dont see how anyone could have ever diagnosed this unit as being low.
Lets hear it!
Andy
The problem is 2nd stage cooling has high head pressure and cycles off the HPS. 1st stage pressures were 75 and 300. 2nd stage pressures will climb slowly and within a few minutes the high side climbs to 400 and the HPS will kick the 2nd stage off. The suction climbs to about 85.
The condensor coil is spotless, now. Before I foam-brited it the 2nd stage would cycle after about 20 seconds of runtime. After the cleaning, the 2nd stage would run for about 2 minutes.
I recovered 1 pound of refrigerant yesterday out of the 2nd stage yesterday, just as a temporary fix to get the head pressure down so they could have the 2nd stage running even if it is a limited capacity. Its been in the 90's and this unit is in a bar. I shut the unit down for an hour yesterday to clean the coil and they about ran me off. I got the head pressure down to about 360 steady and the suction dropped to about 70.
My next step is to recover everything out of the 2nd stage and weigh the 9lbs 6ounces back in. This would eliminate the possibility of being overcharged. I would have recovered everything out of the 2nd stage yesterday but all my cylinders were full. But, I'm real sure its not overcharged. I dont think anyone but me has worked on it. And, if someone else did have their gauges on it, I dont see how anyone could have ever diagnosed this unit as being low.
Lets hear it!
Andy