06-17-2009, 08:06 PM
Working on a lennox 5 ton gas pac ,scroll compressor, R22 TXV metering device. 100 degree ambient temp
Tripping on HP switch.
Hook up gauges and reset switch, Pressures are perfect, check air flow and temp splits all groovy...
I have unit jumped out locally so I pull my jumper and think I see the problem...
Unit shuts off but only suction pressure raises up:confused: Head pressure stays almost the same and SLOWLY begins to fall, I mean slowly....
3 minutes HP fell 5 psi, 10 minutes and pressures still have not equalized (still 100 PSI difference)...
I'm using a recently calibrated set of JB digital DM-2 gauges with standard hoses (non low loss), shraders are functioning properly.
Your thoughts?