07-07-2009, 11:01 PM
Replaced Trane Rotoloc compressor ( liquid bypass stuck open) Pressures unknown...

Pulled out 9Lbs R-22 before swap...

Replace compressor, charge in 9 lbs R-22 liquid bypass on new compressor opens... Liquid line from condenser starts freezing up....

Yes, I said the liquid line is freezing up:eek:

Pull cover off of condenser and see a small torpedo filter drier that is the flash point (ahhhhh obstruction). Pull little drier and put in a full size Sporlan.

While working I happen to notice the data plate, Factory charge 5 lbs...

This is not good at all....

Start recharging after drier swap, things are going well until I hit my head pressure top end and am still below freezing on the suction (5.5 lbs with liquid bypass closed):mad:

WTF.... check blower airflow (supply and return good), Pull evap coil (clean)....
Pull #80 orifice (clear)

Here are my thoughts, Someone before me overcharged this system ( probably charged it while the bypass was opening:eek:) thinking it was just low charge, The origional problem was / is a system obstruction.

I'm going to focus my attention on the evap coil ( partial clog at distributor) and go from there.

Your thoughts?