Re: Understanding Boiler BTU Rating
You have been given some Great advise in the previous posts, it is very true that free sizing has no commitment to accuracy, they don't care if it is a little too big and wastes your money. Ask a contractor if they personally do the heat loss (heating) or Heat Load (cooling) calculations, then pay them to do it with the understanding that the cost is deducted from the job if you proceed. Then no one has anything to loose, contractor or yourself.
As for the BTU ratings of your equipment it works like this:
Highest Btu rate is the energy input (150,000)
Next highest rate is the output depending on efficiency when your boiler is installed in a heated space (78% eff. = 118,000) But if your boiler is installed in an unheated space then look for the lowest BTU rate as this is the absolute minimum output your equipment is capable of. Heat loss happens everywhere and you do need to account for the space where your boiler is installed, not to heat it but for the energy it consumes from your boiler whilst running to heat the rest of your home, this includes the uninsulated piping you have in that same area. Ask your contractor if he has downloaded the free Taco Flopro designer software, it can size a heat loss for a home fairly accurately in about 20 min. of untrained use. Just make sure your wall thickness, insulation properties, room and window sizes are accurate. Good luck.
|