has anyone grooved 10in sch 80 pvc pipe and if so can you tell me how it worked out. I have a job coming up and would like to groove it rather then glueing it.
Reply With Quote
  #2  
Old 08-22-2000, 12:25 PM
JOEH JOEH no ha iniciado sesión
Junior Member
 
Occupation: Ind. Engineer
Location: Hayward, Ca., USA
Join Date: Aug 2000
Posts: 9
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
Post

Mike, I grooved some 6" pipe and used an o-ring in the groove. My application was for a vacuum dust collector system. It has worked well, plus I can take it apart if I need to.
Reply With Quote
  #3  
Old 09-04-2000, 11:10 AM
electrician electrician no ha iniciado sesión
Junior Member
 
Join Date: Aug 2000
Posts: 9
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
Post

I can see how it would work on a vaccum system but what about 40-50 lbs of pressure?
Reply With Quote
  #4  
Old 12-20-2000, 08:03 PM
Frank Frank no ha iniciado sesión
Junior Member
 
Occupation: 3rd yr plumbing apprentice
Location: Edmonton, Alberta, Canada
Join Date: Dec 2000
Posts: 11
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
Post

We have often grooved sch 80 PVC of varying sizes, no problem but you must derate the pipe 50%. presure I'm talking
Reply With Quote
  #5  
Old 01-02-2010, 01:05 AM
MLHardy MLHardy no ha iniciado sesión
Junior Member
 
Occupation: Engineer
Location: Salem, Oregon
Join Date: Jan 2010
Posts: 1
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
Default Re: sch 80 pvc

I worked on a project about 10 years ago that used grooved Sch 80 PVC for chilled water distribution. They had problems with gasket leakage because the installer did not allow for thermal expansion/contraction. PVC expands/contracts 5x more than carbon steel.
Reply With Quote
Reply

Bookmarks

Tags
pvc, sch

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:38 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.