Question

Ok, I need to get smart on this. I have an 80% efficent furnace, 10K BTU venting into a masonry chimney with a 6" clay tile flew. IN addition, we have our water heater venting into the same chimney. Now, I was having some problems last winter, excessive moisture, ignitors not lighting, draft inducer motor died, rusty gas valves, from condensation apparently forming in the 6" clay tiles and running back down. I have been told I need a chimney Liner. Now I have gotten price quotes, ranging from 275.00 to well over 1000.00. That in and of itself sends up red flags right there. Now I have had one contractor that has told me that he might only be able to get a 3" liner in there, so he will have to leave it uncapped and allow the water heater to vent on the outside of it. That sounds wrong to me. I Have had another contractor tell me that since my chimney is within the house walls except for the attic and the few feet outside, i should not need a liner and need something else, possibly a new furnace. I went and checked out a book from the library and that confused me. I went to the local supply house and spoke with someone there, and they told me the following.....

Based on the BTU output of my furnace and water heater, that I need a 4" liner OR 4" "B-Vent". Both of which should fit no problem in the 6" clay chimney tiles. (by the way the masonry for the chimney is completely straight all the way up).

Now that being said, he told make sure I have the contractor use a 4" wye with the wye pointing down. Run the furnace into the straight portion and the water heater into the wye portion. I can use single wall inside but must use either the double wall OR the liner once the pipe heads into the chimney.

After researching and reading, from what I can gather, when a new home is built today, they use "b-vent"" up and out the roof. When we have to retrofit a chimney, we essentially put a new construction flew inside the masonry box? Is that correct?

How much should I expect to pay (fair price) for such a job?

Is the supply house and my understanding correct or do I need to take more into consideration?
__________________
\"A SHIP OF WAR IS THE BEST AMBASSADOR\"<br /><br />OLIVER CROMWELL
Reply With Quote
  #2  
Old 09-09-2005, 01:23 AM
BILLG's Avatar
BILLG BILLG no ha iniciado sesión
Senior Member
 
Occupation: hvac
Years Experience: 30+
Location: caledonia wi usa
Join Date: Jan 2001
Posts: 196
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
Post

Where did you get a 10,000 btu 80% furnace from? I've never seen one. Most likely it's a 100,000 btu and you're just reading it wrong. If it's a 100,000 btu furnace and 40,000 btu water heater, depending on your chimney height, either a 5 or 5.5 inch chimney liner is required. Cost at the very least $500.
Reply With Quote
  #3  
Old 09-09-2005, 01:52 AM
spacebluesonoma spacebluesonoma no ha iniciado sesión
Senior Member
 
Occupation: Navy Recruiter (CRF)
Location: chicagoland
Join Date: Mar 2002
Posts: 966
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
Post

my apologies, 100,000BTU, i fatfingered it.

Ok now, what formula are you using to figure that out? The reason I ask is that it was put to me by someone who said 140,000 would be a 4" liner

Thanks for the help
__________________
\"A SHIP OF WAR IS THE BEST AMBASSADOR\"<br /><br />OLIVER CROMWELL
Reply With Quote
  #4  
Old 09-09-2005, 11:20 AM
BILLG's Avatar
BILLG BILLG no ha iniciado sesión
Senior Member
 
Occupation: hvac
Years Experience: 30+
Location: caledonia wi usa
Join Date: Jan 2001
Posts: 196
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
Post

I have charts but you can look here.

http://www.hartandcooley.com/vent/si...ner_sizing.pdf
Reply With Quote
  #5  
Old 09-09-2005, 03:27 PM
spacebluesonoma spacebluesonoma no ha iniciado sesión
Senior Member
 
Occupation: Navy Recruiter (CRF)
Location: chicagoland
Join Date: Mar 2002
Posts: 966
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
Post

Thank You. Two other contractors have come in and said I need 5" liner.

Now here is the one last concern, when we bought the home it had a Goodwin GMP100-3 that was put in 1994 and has seen a lot of condensation back into it for the past several years. Lots of rust and such inside. Anyway if this thing goes out in the next few years, can I put a 90% efficent furnace in and use the 5" liner or will it have to be changed?

Thanks for everything Bill

Ed
__________________
\"A SHIP OF WAR IS THE BEST AMBASSADOR\"<br /><br />OLIVER CROMWELL
Reply With Quote
  #6  
Old 09-10-2005, 03:32 AM
BILLG's Avatar
BILLG BILLG no ha iniciado sesión
Senior Member
 
Occupation: hvac
Years Experience: 30+
Location: caledonia wi usa
Join Date: Jan 2001
Posts: 196
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
Post

Liner should be ok for water heater alone, and the 90% furnaces vent through sidewall or roof with pvc.
Reply With Quote
  #7  
Old 09-10-2005, 10:22 AM
spacebluesonoma spacebluesonoma no ha iniciado sesión
Senior Member
 
Occupation: Navy Recruiter (CRF)
Location: chicagoland
Join Date: Mar 2002
Posts: 966
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
Post

Thanks again for the help Bob.

Would you believe I have had price quotes from everything 275.00 to over 1000.00 to do the job? One clown wanted to go with a 3" liner for the furnace and vent the water heater around it. Trew him out of the house.

I hate dishonest contractors
__________________
\"A SHIP OF WAR IS THE BEST AMBASSADOR\"<br /><br />OLIVER CROMWELL
Reply With Quote
  #8  
Old 09-10-2005, 09:23 PM
plumber plumber no ha iniciado sesión
Senior Member
 
Occupation: industrial/commercial plumber
Location: Illinois
Join Date: Jan 2005
Posts: 716
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
Post

Space,

Call the Attourney General and the BBB about the idiot that wanted to give you a 3 inch flue up the chimney for your furnace and send the water heater flue gasses up the outside of the flue pipe in the chimney. This is so wrong that the authorities need to know about this guy before he kills someone with carbon monoxide.

He may not be dishonest but if not then he is very uninformed or stupid. All three are reasons to keep or get him out of the mechanical trades.

Google up carbon monoxide poisioning and you will find that it is the leading cause of accidental deaths in the home in the USA. You might save a life.
__________________
Work hard, Play hard, Sleep easy.
Reply With Quote
  #9  
Old 09-10-2005, 10:15 PM
BILLG's Avatar
BILLG BILLG no ha iniciado sesión
Senior Member
 
Occupation: hvac
Years Experience: 30+
Location: caledonia wi usa
Join Date: Jan 2001
Posts: 196
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
Post

plumber, you think that's bad, I replaced a furnace in a house and there was no hole in the flue tile. The furnace that I replaced was their second furnace.



This is also a nice touch.

Reply With Quote
  #10  
Old 09-11-2005, 12:53 AM
plumber plumber no ha iniciado sesión
Senior Member
 
Occupation: industrial/commercial plumber
Location: Illinois
Join Date: Jan 2005
Posts: 716
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
Post

Bill,

Sometimes I think a few of these contractors should go to jail. They should get highly publicized trials and forfiet their equipment.

We are coming up on the heating season again and more people will die because of incompetent or crooked contractors. It will take a congressmans mom to die because of negligence before anything is done.
__________________
Work hard, Play hard, Sleep easy.
Reply With Quote
Reply

Bookmarks

Tags
confused

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 06:44 AM.


Powered by vBulletin® Version 3.8.3
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.