You are currently viewing our boards as a guest which gives you limited access to view most discussions and limited access to our other board features. By joining our FREE community you will have access to post topics, reply to messages, communicate privately with other members (PM), respond to polls, upload content, view attachments, access to the Image Galleries, RIDGID Chat Access ,and access to many other special features. Registration is fast, simple and absolutely free so please, join our community today!
If you have any problems with the registration process or your account login, please contact contact us.
|
Condensate Drain Vent
 |
 |

08-24-2005, 06:24 PM
|
|
Junior Member
|
|
|
Join Date: Aug 2005
Posts: 3
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
|
|
Hey'all
Condensate drain line does not appear to be working right. It doesn't seem plugged. I checked pitch of drain/unit and it's OK. Someone had plugged the vent on the drain at the unit. Since unit is pulling a negative I "unplugged" the vent. Condensate is still building up and overflowing in the pan. What's up with that?
|

08-24-2005, 06:41 PM
|
|
Senior Member
|
|
|
Occupation: industrial/commercial plumber
Location: Illinois
Join Date: Jan 2005
Posts: 716
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
|
|
Can you see where the end of the condensate drains out?
How long is the condensate line?
If possible take a small hose and push down past the tee where the drain comes out of the unit. Try to run some water through the condensate line watching to be sure you don't run any back up into the pan under your evaporator.
To really be sure it is good and clean you can do this: If there is room to cut the line free from your unit and still reconnect it with a coupling then go ahead and cut the line. Then take a garden hose and hold tightly to the end of the pipe. Run water through the pipe until you have a solid stream at the other end. Check the floor drain or what ever your condensate drains into to be sure it is not plugged also so you don't end up with a bigger mess than you started with.
You can jury rig a fitting on the end to allow for a solid connection where you put the hose but it should only take a few monments to blow the snot (the general consistancy of a condensate blockage usually looks like nasal mucus) out of the pipe.
Let us know how it went.
__________________
Work hard, Play hard, Sleep easy.
|

08-24-2005, 06:57 PM
|
|
Junior Member
|
|
|
Join Date: Aug 2005
Posts: 3
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
|
|
Thanks for the suggestion. The real head scratcher I had was whether there should be a vent there or not. I will definitely give the old drain clear out a try.
|

08-25-2005, 02:36 AM
|
|
|
TYPICALLY THE DISCHARGE END DRAINS TO A SINK TAILPIECE. A SHOP VAC CONNECTED TO THIS LINE WILL USUALLY HELP MOVE IT ALONG. ALSO A BLAST OF COMPRESSED AIR WILL BLAST IT FREE. JUST WATCH OUT FOR THE MUCK. IT WILL END UP WHERE YOU DON'T WANT TO CLEAN. A VAC IS MUCH CLEANER.
ALL THE MUCK THAT IS STCUCK IN THE PIPE CAN BE WASHED AWAY IF YOU CAN ESTABLISH FLOW. ALSO A SMALL FISH TAPE OR 1/4'' CABLE CAN ALSO BE RUN FROM EITHER END. YOU PROBABLY WON'T GET PAST A 90 TURN. SO TRY FROM BOTH ENDS. YEARS OF BUILT UP MUCK MIGHT TAKE SOME EXTRA EFFORT.
DEPENDING ON THE HUMIDITY AND THE SIZE OF THE UNIT, YOU CAN HAVE 5-15 GALLONS OF CONDENSATE FORM A RESIDENTIAL UNIT, PER DAY. LOTS MORE ON A COMMERCIAL SIZE UNIT.
JUST THINK A LITTLE SWEAT WILL PAY OFF WITH A COOLER, DRIP FREE UNIT.
GOOD LUCK RICK.
|

09-30-2005, 12:37 PM
|
|
Member
|
|
|
Occupation: Retired
Location: Jessup, MD
Join Date: Sep 2005
Posts: 32
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
|
|
My PVC Drain lines always get plugged with dust. So the pan overflow was always dripping on the floor. I just put a piece of 1/2 inch clear on the end of it and routed it down the drain. Usually once a year I'll go inside and blow all the junk out of the PVC.
|

04-07-2006, 04:24 PM
|
|
Member
|
|
|
Occupation: Plumber
Location: Grimsby Ontario Canada
Join Date: Mar 2006
Posts: 98
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
|
|
also
Also you must make sure you fill the trap on the condesate line before you start up the unit or else it will not be able to start draining. (just sucking air into the unit) The vent (after the trap) should be left opened to eliminate the slight chance that the trap would be siphoned. (very unlikly but i guess possible) try draining when the unit is off to make sure the unit is not sucking the trap back into it. I guess this is not a problem since it has been working at one time. so as the others said a good clean is probably all it needs
|

04-07-2006, 04:29 PM
|
|
Member
|
|
|
Occupation: Plumber
Location: Grimsby Ontario Canada
Join Date: Mar 2006
Posts: 98
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
|
|
also
Also you must make sure you fill the trap on the condesate line before you start up the unit or else it will not be able to start draining. (just sucking air into the unit) The vent (after the trap) should be left opened to eliminate the slight chance that the trap would be siphoned. (very unlikly but i guess possible) try draining when the unit is off to make sure the unit is not sucking the trap back into it. I guess this is not a problem since it has been working at one time. so as the others said a good clean is probably all it needs
|

04-08-2006, 01:20 PM
|
 |
Senior Member
|
|
|
Occupation: Retired
Location: Fort Smith, Arkansas
Join Date: Dec 2005
Posts: 543
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
|
|
Mine used to overflow the pan, took me awhile to figure it out. The line looked level, but after putting a level on it it was running up hill. We all know water does not run up hill.
__________________
SSG, U.S. Army
Retired
K.I.S.S., R.T.F.M.
|

11-16-2006, 10:37 PM
|
|
Junior Member
|
|
|
Occupation: Hvac mngr
Location: Rochelle, Il.
Join Date: Nov 2006
Posts: 29
Nominated 0 Times in 0 Posts
Thread of the Week Award(s): 0
|
|
you shouldn't have a vent on your drain unless it is after your trap. You do have a trap don't you?
|
 |