standpipe height
  • standpipe height
    What is code for standpipe height at a washing machine? I know 2" diameter and venting. Is it distance from the floor? Length of pipe above the trap? I have had responses from two plumbers and a city plumbing inspector and had three different answers. I live in Alberta.
    Cheers.
    Re: standpipe height
    Trap wier no higher than 18" no lower than 6" from floor.
    Standpipe from wier no shorter than 18" no longer than 30"
    UPC
      Cheers.
      As of august they now want a 2'' trap - top of stand pipe min 32'' from the floor. Standpipe cannot be more then 36'' - trap weir to above F.L.R.
      NPC 2.4.2.1
        Once again, different code answers for the same question from everywhere. But of course every code just has to be right.
          Cheers.
          Dirtyhands is right 18-30" for UPC. However you are in Canada so the trap wier can't be higher or lower than a beer can. Not a US beer, it has to be one of those high alcohol content Canadian beers. Then the standpipe can be 4 to 8 beer cans high
            2.4.9.3.3 (appendix A) is the clause in N.P.C for washer stand pipes. top of stand pipe 32 inches (810 mm) mininum from floor , 24 inches (610 mm) minimum length, 36 inches (900mm) maximium length
              Have you seen the recent Standata?
              http://www.municipalaffairs.alberta....hesWashers.pdf
              You will never expand your mind, if you do not challenge your beliefs.
              By the reading of this post, you acknowledge and agree that the poster shall not be responsible or liable, directly or indirectly, for any damage or loss caused or alleged to be caused by or in connection with use of or reliance on any content contained herein.
                Can we make up our minds about this Code in AB...They really like to change this code up.
                West Trail Mechanical Ltd
                www.westtrailmechanical.ca
                  36" I keep it level with the kit counter
                    code in Ohio says the standpipe has to be a minimum of 18 inches and a max of 42 inches above the trap weir . The trap needs to be at least 2 inches and drain into a 3 inch branch
                      same here as in Ohio then, except we aren't required to use a 3 inch branch. Though I remember that being an amendment to the North Carolina code when I worked there.
                        NC:
                        2" Standpipe
                        2" Trap
                        35" above the finished floor
                        24" Minimum
                        48" Maximum
                        No trap on an exterior wall unless 2"x6"
                        Increase drain to 3" within 6'
                        No crown vent
                        If copper pipe-must have hammer arrestors on the box
                        No drilling 2" pipe horizontally through ANY studs. Doubled or non load bearing.
                          Yes, HondaHead I have seen the standata. With our hard water suds are something seldom seen.
                            NC:
                            mild curiosity, What's that all about? does it only apply to 2x4?
                              Yes. Only 2"x4". Not enough wood left to meet code.