venturi tees
  • venturi tees
    i will be helping a friend install a HW toekick heater in a kitchen remodel. should venturi tees be used as part of the install? the house has 3/4" copperfinned baseboard and the kicker has 1/2" copper tubing. the manufacturer instructs that a regular 3/4x1/2x3/4 tee be used to supply water to teh kicker. the water leaving the kicker should be reintroduced into the 3/4 copper via a 3/4x1/2x3/4 venturi tee. their position is that the venturi tee is on the return line as its purpose is to create enough back pressure to onduce water to enter the kicker via the regular 3/4x1/2x3/4 tee. any thoughts on this?
    Re: venturi tees
    As far as I know, venturi tees should only be used on one pipe systems. But I suppose the manufacturers spec takes precedence.
    West Trail Mechanical Ltd
    www.westtrailmechanical.ca
      Re: venturi tees
      I have installed them for years that way with no problems, just make sure you bleed all of the air out of the system and it will work fine.
        Re: venturi tees
        If the fintube you are connecting onto is on same level as kicker then one monoflo tee is fine. If you are piping down 1 floor level or up 1 floor level I use a monoflo tee on both sides.
          Re: venturi tees
          very good bill thats what i was going to say
            Re: venturi tees
            is there a minimum distance which should be maintained between the tees, assuming same level plumbing?
              Re: venturi tees
              I was taught 18" we will soon see if anyone disagrees.....
                Re: venturi tees
                I was always told 10 pipe diameters of straight pipe.
                  Re: venturi tees
                  The old rule was 10 pipe diameters but I like to go a bit more with 3/4" copper. 18" will work. Make sure to look at the in and out arrows on the fitting. Installed backwards they will actually work but produce a lot of turbulence and loss of flow.