power vent hot water heater problem
  • power vent hot water heater problem
    HI We have a AO Smith FPSH-50 power vent hot water heater that lights for 5 seconds than goes out, until you turn the dial on the temp setting,than it will be ok for a day or so.Than it starts all over turn the power switch off and on than it relites and you have change the temp setting to get it to stay on
    Re: power vent hot water heater problem
    Hot surface ignitor/flame sensing rod
      Hi Igniter is turning red and lighting gas.flame sensing rod? do not see it on the parts list or a picture of it by the burner Thanks
        Lets back up.
        Can you tell me the series number? the series number is a (usually) 3 digit number after the model number. Example: FPSH 50 248
          Originally posted by jody1979
          riproarin, i think you should call roto rooter plumbers. i called them last night, and they came out right away to fix my problem!
          Now there is some good advice.
            A couple of years ago we got a call from a GC about a house we had done for him a few years before where the owner had called Roto Rooter to replace the water heater. The RR guy hooked up a new conventional water heater to the existing power vent flue. Of course the flue pipe melted. Fortunately, it didn't set the house on fire before we were alerted. Mighty embarassed RR manager met us and GC at the house. He couldn't eat enough crow. GC stuck him with our bill to correct the error and a threat to call in the authorities if there was the least complaint on the part of RR. HO got a free heater. Lucky she didn't lose her house. She couldn't explain why she didn't call us first. HO's are a wierd lot. Necessary evil, I guess.
              jody 1979: We all know you are a spammer for roto rooter, so BUZZ OFF!!!!
                series number 252
                  series number 252 serial number MEO!-0014406-252
                    That heater has a Honeywell Smart Valve. It will flash an error code when it doesn't light but it should keep trying after an hour.
                    Page 28 shows the sequence of operation for your heater and error codes
                    http://www.hotwater.com/lit/training/tc048r6.pdf
                      Hi Thanks manual should be big time helpful in figuring out once in awhile heater problem.Heater has been no problem since moving temp sensor knob back and forth and resetting to a slightly lower temp
                        Hi Heater still working but not proper will go thru cycle than flash 6 times.Can fush with temp control and heater will relight and work proper for a day or so.
                          Did you troubleshoot it or just keep flipping the dial back and forth?
                          Did you even read the manual?
                          6 flash error code:
                          1. Reversed polarity in 115 volt power supply.
                          2. Heater/burner not properly earth grounded, check pin 3 on wire harness plug (valve end) to burner tube for 115 volts, check ground path to burner.
                          3. Ground fault interruption (GFI) breaker causing intermittent operation, try non-GFI outlet.
                          4. Flame sense rod dirty or incorrectly positioned.
                          5. Vent system length exceeded, too many elbows,
                          6. Flame sense/HSI wiring condition/connections.
                          7. Low or no supply gas pressure.
                          9. Damaged, defective, or incorrectly positioned HSI
                          Number 1 and 2 are most likely the suspects.
                            Hi Yes read the manual heater is 5-7 yrs old and has been working great so 1and 2 did not seem practical.#3 no gfi #4 have not pulled burner out yet to check flame sensing rod #5 vent system short and direct 2 elbows.#6 ignorant about what a HSI is?didnot check 7-9 Will go back and check 1-2 never know and that would be easy and inexspensive Thanks
                              Do a google search on what a flame sensor rod is and give a a cleaning then enjoy your hot water.This is a VERY common problem.
                              What do you guys like for cleaning these?
                              I like steel wool but have heard some guys use emery cloth!