Double Washing Machines on 2" pipe?
  • Double Washing Machines on 2" pipe?
    http://farm3.static.flickr.com/2587/...2a55b410_o.jpg
    I'm putting in two back to back washers for my basement laundry room and in-law sweet bath as shown in picture.
    I have an existing 2" drain coming out of concrete floor, everything else is planned.
    I plan to put a clean out near floor followed by a double wye, or possibly 2 stacked single wyes. Above the wye(s) will be a 2" vent to basement ceiling vented to side of house.
    My question:
    (1)
    Will the 2" drain line be capable of draining 2 washers as shown in picture?
    • The books i've seen list the fixture unit FU of a washer at 2 (it was 3 in another book), with a total of 4-6 for the 2 washers.
    • Additionally, the given maximum FU of a verticle 2" pipe is listed as 10 and the max FU of a horizontal 2" pipe is 6.
    • The vertical 2" pipe coming out of floor quickly changes to a vertical 3" pipe just below the slab by way of a 3/2 bushing. From there the 3" pipe drops another foot into a 3" 90 and short horizontal run to the 4" main drain.
    • There is never a horizontal 2" segment of pipe carrying double capacity.
    it is all planned at the moment. Don't tell me to tear up concrete
    Re: Double Washing Machines on 2" pipe?
    No license or permit?...then no problem.
    Should work. Go with 2 wyes instead of dbl. wye.
    Increase drain riser to washer to at least 30".
    May have a problem if both discharge at same time.
    Or not.
      So given a vertical 2" pipe coming out of the slab... This would be the best solution, other than breaking up the concrete slab and changing to a 3" pipe (which an inspecter would recommend)?
        You say it goes to 3" just below the slab on the vertical?
        Shouldn't be a problem.
          I wouldn't put both on a 2" vertical. That's back to back with pumping action.
          And no WYE's legal here off the trap arm. Right? IPC?
            Aw, c'mon. Where's your sense of adventure.
            No license, no permit, no problem.
              here is what is below the slab. So JC you think I need to tear out the concrete and expend the 2x4 wall to allow for the 3" pipe?
              If the two washers can't drain on a vertical 2 inch, that is a better situation than a flooded living area.
              will the vert drop of a wye affect the vent in IPC? So you think i need to bring the 3 inch up thru the slab and have stacked 3x2 sanitary Tees to each washer?
                The Fla. Code, Sec. 406.3 states:
                "The automatic clothes washer fixture drain shall
                connect to a branch drain or drainage stack a
                minimum of 3" in diameter."
                Which yours does, eventually.
                Your area may be different.
                The inspector rules.
                  Three inch trapasaurus megasus.
                    Hahahaha, "trapasaurus megasus". I got a kick out of that.