Need education in Electrical Mathemetics.
  • Need education in Electrical Mathemetics.
    I need a little help with watts. I have a 4800watt construction heater. Does the rating 4800 watts mean 4800 watts per hour?
    Am i correct in saying that if my heater ran for 1/2 hour per hour I would be using 2400 watts?
    Trying to figure out my heat loss in a building in BTU's. Converting watts to BTU's is easy.
    TIA,
    Chris
    Re: Need education in Electrical Mathemetics.
    You need to get your units straight. If an item consumes 4800 watts, then it uses 4.8 Kilowatt Hours. ( Electricity is billed in KWH ). So, yes, if it ran for 30 minutes, it would use up 2400 watt hours ( 2.4 KWH).
    Similarly, heating and cooling would be talked about in BTU PER HOUR.
      The heater would consume 4800 Watt Hours over one hour of continuous use. One KWHr. (Kilo Watt Hour) is equal to 1000 Watt Hours.
      In case you need it figure on 3412 BTU Hr. per 1000 Watt Hours for a resistive element electric heater such as your's.
      Hope this helps you some.
        The heater is only running 7 minutes/hour @ 10F. so if my math is correct I am only using 560 watts or about 2000 btu's ......
        Thanks for your help Gentleman.
          When the heater is cold it uses more power (draws more current).
            great tips. I enjoyed reading this
            soapstone
              its just the maximum power or wattage output that it generates, not nessisarly what its always going to run at. you really need to know the voltage and how much current (amps) is being drawn.
              for instance 120v generating 2a 120*2=240watts