Radiant Floor Heat
  • Radiant Floor Heat
    I am remodeling a bathroom and my customer would like to get rid of his steam radiator and install radiant floor heat. Running a new circuit to the electric panel however is impossible. There is a window air-conditioner in the bathroom on a 220 circuit. Which of course won't be used in the winter when the heat is needed.
    My question is if its possible to use the air-conditioner circuit for the floor heat. The heating pads for this size (4'x4' max) are rated 120V... there is a thermostat control for the floor thats rated for 120/240 but the small pads are 120. Can I use this control with a 120 pad on 220 circuit?
    Clear as mud?
    Thanks in advance!
    Re: Radiant Floor Heat
    power here in the US. split phase for residential.
    the 220 volt circuit can supply the controller and the pad but you need to know what you are doing on this
    this needs to be done properly by an electrician
    if you are not an electrician please call one on this
    coffee hell gimme booze!!!
      Probably not. The breaker is sized for the AC and likely not sized for your circuit too. If an older 3 wire ckt, you cant use it. Moreover, nearly always a radiant heat mats need GFCI protection (which you probably don't have). The listing instructions usually call for a dedicated (individual) circuit.
      I agree with the others, hire an electrician and have the piece of mind of knowing it's done right.
      Also, the wiring methods need to be compliant. (it would suck if the inspector made you rip up the new floor!)
        thanks i forget to mention the breaker
          Oullet makes a 220 volt radiant mesh. Their controller also has GFCI protection internal to the unit. The breaker would have to be changed out to the size required by the mesh. I think the 220 volt version starts above 60 sq ft.
            No, I don't think this will fly;
            The AC wall unit is most likely a dedicated outlet and is allowed to be rated at 80% of the branch circuit. If you add the radiant heat to this outlet the AC is now only allowed to be rated at 50% of the circuit rating. Example; Your ac draws 16 amps and is on a 20 amp breaker with #12 wire. But now, you would need to wire a 40 amp circuit just to add the heat, which would require #8 wire!
            See Art 440.62 of the NEC
            There is an exception that would still allow the 80% rating, but it would need to be electrically interlocked to prevent simultaneous operation.
              I was under the impression that the AC would be abandoned. It would have to be one or the other, not both.
                right Im used to installing the combination ac and heater units that are used in some of the offices. and hotel rooms
                these were wired using #8 wire for the larger ones and 10 for the smaller
                these were usually equipped with interlocks
                  It will be always good to take the help of electrician to install the radiant floor heating properly.
                    Even we recommend using a Qualified Electrician for this type of work downunder. What you think is impossible a good Qualified Electrician may be able to do with his eyes closed and his/her hands tied behind their back.
                    The Engineers of this world hate this but USE A PRO..................!!!!!
                      For a while in the late 70's a system of ceiling radiant heat was used
                      where the sheet rock had a wire mesh system in place.
                      This was one of the many unique systems of the time due to the energy crisis.
                      Always wondered how they faired.
                      Most ceilings need repair over time with water damage or change in texture, remodels and such.
                      Back then we had Earth homes, Hay bale homes, envelope homes and one I worked on, a cardboard home.
                      New ideas were rampant when oil was in short supply, it was a different time.