  • 2 breakers one light

    I have a situation were it takes turning off two breakers to turn off one light. Is there a safety issue I should worry about this and if so any ideas on what would cause this.

    Thanks

  • #2
    If this is true, you should trace to the point of cross connection. Apparently someone tied two circuits together. This would be in one box. Probably a 12/3 or 14/3 romex. You can tell this by looking in the panel at the wires that go into the two breakers you must turn off. Then trace to the first j-box.

    Comment


    • #3
      You need to fix this. Since 2 breakers are feeding one line if you have a problem you can supply twice the rated current to the wires after the junction point which could result in a fire