How do you check charge?
  • How do you check charge?
    How many guys out there use superheat/subcool to check charge? Or do you use 75/220 or the personal favorite "beer can cold" method
    Re: How do you check charge?
    sorry i dont do service
      on new systems I weight it in, this is the most accurate way to charge. on existing systems I use superheat or subcooling.
        Same here Bill. If the ductwork is remotely close to being sized right I'll weigh it in. Most of the time the sticker on the unit that notes the factory charge, is right. Ive run across some Junkitrols that stated a number 3lbs less than what was needed.
          How does the duct design dictate the charge? I'm glad to see we're doing it right. The hacks around here is the "beer can cold" method.
            you need very close to 400 cfm per ton on standard units. you can sometimes if your in a pinch slighty improve performance on units with improper air flow by adjusting refrigerant charge.
            it is always much better to correct air flow and charge correctly
              im all about superheat and subcool. i think it is by far the most accurat, but the most time comsuming. by switching from weighing in i have noticed a diff on freformance, especially due to unnaccurate factory charges.
              how is it that so many answers are in the instructions
                For instance if you have a 3 ton system and ductwork sized for a ton and a half you will have low indoor airflow which will likely show up as a low superheat/high subcooling.
                  Makes perfect sense, never even occured to me. Learned something new tonight.
                    it wil throw off your readings which is the whole purpouse, that would be too big of a gap to have a proper system. ultimitly if you have 50 degree air coming out of your registers your cooking with gas as they say