Power venter connetion

Page Title Module
Move Remove Collapse
X
Conversation Detail Module
Collapse
  • Filter
  • Time
  • Show
Clear All
new posts

  • Power venter connetion

    There is a power venter on the cilling connected about 8" C vent in a coffee shop kitchen.

    I have found that the installer connected the power venter and the pipe with duck tape, but the pipe was fallen by the weight.

    The material of power venter is cast iron or similiar. I was going to drill 3 holes to connect the vent pipe with power venter. Before I do it, I better to ask you.

    Duck tape connection does not stay long.

    Please give me some advice.

    Thank you.
    Attached Files

  • #2
    Re: Power venter connetion

    Hose clamp.

    Andy

    Comment


    • #3
      Re: Power venter connetion

      I checked 5 HVAC and plumbing supplier but noone has 8" size.

      Just 6" or 10"

      Comment


      • #4
        Re: Power venter connetion

        Get a 6 and a 4 and put them together end to end.

        Andy

        Comment


        • #5
          Re: Power venter connetion

          Thank you!

          I will try right away!

          Comment