  • Thermostat wire

    A technician needs to run some 24 volt thermostat wire 75 feet. To avoid a voltage drop, the technician should use:
    A. 16 awg
    b. 18 awg
    c. 20 awg
    d. 22 awg

    Later, JONESY

  • #2
    Re: Thermostat wire

    (B) 18 AWG

    But I would bet that you would not get a drop that would make a difference in system operation using any of these, we are only talking 40 VA.

    Okie

    Comment


    • #3
      Re: Thermostat wire

      Are these NATE practice questions?

      Comment


      • #4
        Re: Thermostat wire

        Im gonna choose (A) because 75' of thermostat wire is actually a 150' run. You have the same side of the 24v traveling to the stat via the Red conductor then traveling back to the equipment via the White wire.

        Andy

        Comment


        • #5
          Re: Thermostat wire

          No they aren't NATE questions. These are some practice questions from a testing organization out in Illinois. Some are pretty tricky. I'll post some more when I get time. Thanks for the input.
          Later, Jonesy