  • honeywell pro 8000 installed but only heat

    Hello there,
    I got a new thermostat TH8110U1003 today for my upstairs.. this is the second time I upgrade the thermostat to different brand.
    the current settings with (Ritetemp) thermostat is (heat pump without aux).. so the the issue is that I put the same settings for the honeywell and it blows hot air on cool..
    I tried putting it on hold, changing temperatures on schedule moving the system from cool to heat or vice versa.. no success..

    picture of current thermostat


    settings for current thermostat


    the honeywell pro 8000 settings that aren't working correctly..


    would really appreciate it if someone can give me a hand..

  • #2
    Re: honeywell pro 8000 installed but only heat

    Show a picture of the wiring on the Honeywell VisionPro

    Double check your jumpers

    Go through the software setup settings very carefully. It's a great thermostat but it's definately not Plug and Play

    Comment


    • #3
      Re: honeywell pro 8000 installed but only heat

      I think I figured it out.. for the system settings it says #170: System type:
      changed from 1 into 2.. now its blowing cool air and i like it.. the only question is what should I put in #190...
      in the winter I use the heat with (heat pump without aux)



      Comment


      • #4
        Re: honeywell pro 8000 installed but only heat

        let me know.. thanks
        Last edited by Klinzter; 04-15-2011, 07:14 PM.

        Comment


        • #5
          Re: honeywell pro 8000 installed but only heat

          Find out if your heat pump reverses on heat or on cool/

          Comment


          • #6
            Re: honeywell pro 8000 installed but only heat

            how do I find out?

            Comment


            • #7
              Re: honeywell pro 8000 installed but only heat

              Originally posted by Klinzter View Post
              I think I figured it out.. for the system settings it says #170: System type:
              changed from 1 into 2.. now its blowing cool air and i like it.. the only question is what should I put in #190...
              in the winter I use the heat with (heat pump without aux)
              If its blowing cool when turned to cool and blowing heat when turned to heat, 190 is set correctly.

              Andy