Frozen Line set
  • Frozen Line set
    Ive been having a issue with 1 unit in the building. The units line set keeps freezing up. I always was under the impression the only reason a line set ever froze was due to lack of air flow over the coil. Am i missing something here? Also forgot to mention its a TXV valve.
    Re: Frozen Line set
    just the line set and not either coil?
      Re: Frozen Line set
      Yeah sorry coil and the compressor are both freezing up along with the suction line. Ive already cleaned the coil with a foaming coil cleaner and hosed it down pretty well.
        Re: Frozen Line set
        Make sure the evap coil and furnace or air handler blower wheel is clean. Then check the refrigerant charge.
        James
          Re: Frozen Line set
          Sadly both done and its freezing up. The sub cool is dead on. and the evap coil i just cleaned. and still having it freeze up. i also knocked a whole in the door to make sure there was enough air coming into the closet.
            Re: Frozen Line set
            still sounds like an airflow problem. had a similar one where the kids were lounging on the flex duct in the attic for the return. had it nice and flat.
              Re: Frozen Line set
              I'm a lttle confused about knocking a hole in the closet door. Also make sure your supply air isn't blocked. I've had instances where a piece of duct liner came loose and fell onto the evap coil. If everything checks out good with the airflow. Try a new TXV.
              James
                Re: Frozen Line set
                Sorry should have also mentioned that there is no return. the air handler sits in a closet. there is already a vent in the door but i dont belive its big enough for the air flow. thinking this may be the problem
                  Re: Frozen Line set
                  Rule of thumb for sizing a return air grille is 1sq. ft. per ton of cooling.
                  James
                    Re: Frozen Line set
                    just take the door off for a day or two and see if that solves the problem?
                      Re: Frozen Line set
                      well its a 3 ton unit. with 4 sq foot opening. and the door cant come off due to security reasons. work in a hospital
                        Re: Frozen Line set
                        You might want to throw a part at it, being a hospital. I worked at a university for 24 years and didn't have the luxury of spending a week repairing a broken ac. Spent many a 100+ degree days on rooftops working on units.
                          Re: Frozen Line set
                          ran into a similar issue today in a large commercial building. One of the fire dampers had malfunctioned and closed cutting the air discharge in half
                            Re: Frozen Line set
                            Well for temp. I put on a control to only run the fan when the pressures are high to take off the majority of the heat. I guess im just going to have to figure it out. Sadly there is no return duct at all. The unit is 3 1/2 tons. The opening to the door is 4 cubic feet. And the evap coil is clean!!! I acid washed it 3 times. The sub cool is dead on. The great part about this is that its only for a gift shop. So i can play with it at my leisure. Thanks to everyone for trying to help me with this!!!
                              Re: Frozen Line set
                              THERES your problem. If that doesnt solve it, check to see if head pressure is excessivly high. Could have a blockage or crimped line somewhere.