  • ASCO Solenoid Valves

    Installed 3 NC ASCO Red Hat solenoids the other day on a water line going into a chrome fume scrubber unit at a local chrome shop. The shop is in a fairly high pressure water location - id say our main after the city meter runs at about 70-80 psi. The valves were working properly until this morning when one valve wouldn't shut off. Took the valve apart - seat intact, no substantial debris. Took the power completely off just to see if this normally closed valve would hold water - water still getting through. Im wondering if you guys have experienced any malfunctioning of these valves when being used at or close to their max. rated pressure (100 psi on this model). Any thoughts? PRV? Thanks in advance.
    Last edited by doubleD; 04-18-2008, 12:21 AM.

  • #2
    Re: ASCO Solenoid Valves

    70-80 psi isn't a huge amount of pressure. Do those valves have a pressure rating.?
    sigpic

    Comment


    • #3
      Re: ASCO Solenoid Valves

      100 psi max on the model i installed- so you would think 80 psi would be no problem - anyway..i put in a new one today and it held. Just wondering if anybody had similar circumstances

      Comment


      • #4
        Re: ASCO Solenoid Valves

        The only problem we have had is that the Asco 1"solenoid valve was causing a hellacious amount of water shock in the piping. After a lot of "solutions" we installed a slow opening/closing motorized ball valve that seems to have solved the problem. The last problem with the soenoid valve was that it was stuck open.

        After rereading your post it sounds like a debris problem not a pressure problem. If it continues, install a why strainer upstream from the valve.

        Comment


        • #5
          Re: ASCO Solenoid Valves

          If that 100 PSI the pressure rating of the valve body or the MAX process pressure that the valve will maintain closure against? IF NC then all you got working for you is the spring pressure to shut the valve right?

          Do you have a model number for these valves? I can ask around and look in my maintenance DB for past problems such as you are having. But there are so many different models of ASCO SOVs it would be tough to pin it down w/o a model number.
          "When we build let us think we build forever. Let it not be for present delight nor for present use alone. Let it be such work that our descendants will thank us for, and let us think, as we lay stone upon stone, that a time is to come when these stones will be held sacred because our hands have touched them, and that men will say, as they look upon the labor and wrought substance of them, "See! This our fathers did for us."
          John Ruskin (1819 - 1900)