  • Mech. room area drain

    New furnace condensate and T.P. DUMP 6" ABOVE inside area drain . S.F. signed off ,no problem. Who says outside?
    I can build anything You want , if you draw a picture of it , on the back of a big enough check .

  • #2
    Re: Mech. room area drain

    Condensate is ok to dump into an approved receptor per 801.6 and 807.0 of the 2007 CPC. However, if it's acidic it has to be neutralized. Relief valve may discharge at "approved locations" other then outside the building per 608.5.

    Comment


    • #3
      Re: Mech. room area drain

      some townships by me do not allow us to put condensate water into a drain ,it has to go out side or into storm water and floor drains that do not tie into sanitary drains .
      Charlie

      My seek the peek fundraiser page
      http://observatory.mountwashington.o...nal&fr_id=1040


      http://www.mountwashington.org/weather/conditions.php

      new work pictures 12/09
      http://public.fotki.com/hvachawk/

      Comment


      • #4
        Re: Mech. room area drain

        The new 2009 IPC code says the T&P can discharge on the floor.

        Comment


        • #5
          Re: Mech. room area drain

          Originally posted by EasyEman View Post
          The new 2009 IPC code says the T&P can discharge on the floor.
          And they want us to drop UPC and unify under IPC.I guess it will make our job out hear even easier.

          Comment


          • #6
            Re: Mech. room area drain

            Originally posted by Plumbus View Post
            Condensate is ok to dump into an approved receptor per 801.6 and 807.0 of the 2007 CPC. However, if it's acidic it has to be neutralized. Relief valve may discharge at "approved locations" other then outside the building per 608.5.
            It passes through the filter first.
            I can build anything You want , if you draw a picture of it , on the back of a big enough check .

            Comment


            • #7
              Re: Mech. room area drain

              In S.F. sewer and street drains tied togeather.
              I can build anything You want , if you draw a picture of it , on the back of a big enough check .

              Comment