  • Schedule 80 DWV pipe

    Another project we're looking at calls for 4" schedule 80 pvc in a parking lot which is roughly 3 feet deep for about 60ish feet to the manhole. The under slab is schedule 40 ABS. I can find schedule 80 pressure pipe and fittings but not dwv fittings. Any ideas?

    BTW, We have rfi's in questioning the sch of the pipe. the engineer was an idiot imo. We're building to ipc. The sewer line is crossing an existing water line and the prints call for a rebar cage and concrete 5' on each side of the C/L. Where in the heck is this code??!!! This is why we roll up blue prints.....to hit engineers over the head with them.
    Buy cheap, buy twice.

  • #2
    Re: Schedule 80 DWV pipe

    Originally posted by gear junkie View Post
    Another project we're looking at calls for 4" schedule 80 pvc in a parking lot which is roughly 3 feet deep for about 60ish feet to the manhole. The under slab is schedule 40 ABS. I can find schedule 80 pressure pipe and fittings but not dwv fittings. Any ideas?

    BTW, We have rfi's in questioning the sch of the pipe. the engineer was an idiot imo. We're building to ipc. The sewer line is crossing an existing water line and the prints call for a rebar cage and concrete 5' on each side of the C/L. Where in the heck is this code??!!! This is why we roll up blue prints.....to hit engineers over the head with them.
    I'm not sure there are Sch. 80 DWV fittings. You can call Charlotte and/or get test & installation specs. to submit. Might be all you need.

    The "rebar cage" seems to be from the mind and ego of an engineer.

    But in fairness I'm not looking at the prints either. What kind of water line is it? Small 3/4" copper or 6" plastic of some sort?

    If it's a big line it may not be bad to cover your bases with a cage support.

    If not, seems knuckleheadish.

    J.C.

    Comment


    • #3
      Re: Schedule 80 DWV pipe

      When ever drainage is over potable. Potential cross contamination could in theory happen.

      Comment


      • #4
        Re: Schedule 80 DWV pipe

        Hey Ben, They make sch 80 fittings just brace yourself when you get the pricing on them. Just seen paperwork on a 4" sch 80 long sweep st 90 that a local industrial plumbing company brought back to try and get credit for $95 a fitting and they had 12 of them. Make sure if you do buy some that you check on the return policy
        ________
        VAPORIZER FORUM
        Last edited by TOPDAWG; 02-24-2011, 06:30 PM.
        Mike

        Comment


        • #5
          Re: Schedule 80 DWV pipe

          Mike, what company makes them? JC, It's a 4" sewer line going over a 10" ductile iron main. According to IPC, as long as your sewer line is rated for interior use(no clay), the sewer and water can be in the same trench with no seperation.
          Buy cheap, buy twice.

          Comment


          • #6
            Re: Schedule 80 DWV pipe

            IPC
            oopsey

            Comment


            • #7
              Re: Schedule 80 DWV pipe

              Water 12" above

              Comment


              • #8
                Re: Schedule 80 DWV pipe

                So these kooky military engineers are sending you these butterfly valves cause they say "Or equivelent".
                You look at hpde fuseseal or something more common than sch.80 DWV.

                For future renovation

                Comment


                • #9
                  Re: Schedule 80 DWV pipe

                  If it was my store, and the drain line was going under asphalt.
                  You gd right I would want sch 80.

                  Comment


                  • #10
                    Re: Schedule 80 DWV pipe

                    Originally posted by gear junkie View Post
                    Mike, what company makes them? JC, It's a 4" sewer line going over a 10" ductile iron main. According to IPC, as long as your sewer line is rated for interior use(no clay), the sewer and water can be in the same trench with no seperation.


                    Yes, but what is the "intent" of that code or the interpretation. It may be for intended for the one buildings water & sewer.

                    Is the 10" water main only supplying this building? And the DWV only for the same building?

                    If not then code interpretation or local jurisdiction could exclude the IPC interpretation you quote so as to protect others.

                    J.C.

                    Comment


                    • #11
                      Re: Schedule 80 DWV pipe

                      Hey Ben i took these pictures for you this morning, looks like there made by a company called Spears
                      Click image for larger version

Name:	a26e1e8a002b82c87c7e83f60e5888c2.jpg
Views:	1
Size:	49.1 KB
ID:	9458

                      Click image for larger version

Name:	25dabbcf8b3b2e494fd82bef1c6f9f40.jpg
Views:	1
Size:	40.3 KB
ID:	9459

                      Click image for larger version

Name:	432f7205157676905a36ebf704124436.jpg
Views:	1
Size:	46.8 KB
ID:	9460

                      Click image for larger version

Name:	9ae533b82e5e5bed13f371664c84fd28.jpg
Views:	1
Size:	40.2 KB
ID:	9461
                      ________
                      LUCA MARMORINI
                      Last edited by TOPDAWG; 02-24-2011, 06:31 PM.
                      Mike

                      Comment


                      • #12
                        Re: Schedule 80 DWV pipe

                        Spears Sch 80 PVC Fitting Price List.

                        My old company sold Spears fittings for years and they are a very reputable company if you're not familiar with them.
                        Last edited by BadgerDave; 01-08-2010, 03:27 PM.
                        Teach your kids about taxes..........eat 30 percent of their ice cream.

                        Comment


                        • #13
                          Re: Schedule 80 DWV pipe

                          Originally posted by gear junkie View Post
                          According to IPC, as long as your sewer line is rated for interior use(no clay), the sewer and water can be in the same trench with no seperation.
                          Same with UPC (2006). See Section 609.2. But, you do need enough separation to allow for repair.

                          Comment