  • prv valeve

    About an 8 month bradford white 40 gal nat. gas. I had to drain and remove temporally.
    Customer says the prv is letting off a drip and rumbling about every Hr. Will replace the Prv.
    It's set a little high on temp. Any thoughts?
    I can build anything You want , if you draw a picture of it , on the back of a big enough check .

  • #2
    Re: prv valeve

    It'll be pressure, install a PRV w/bypass and an expansion tank. It's incredibly rare for a T&P to fire for temp on domestic hot water systems.