  • LThompson
    replied
    Re: I give up. whats wrong in this picture?

    have to use santee (vent fitt) for trap arm and foot vent needs to vent under sub floor to closest wall with c.o. the pipe at top cannot have flat spot have to use 2 45 and 1 90

    Leave a comment:


  • Bob D.
    replied
    Re: I give up. whats wrong in this picture?

    Originally posted by Plumbfast View Post
    As an added note, at least in PA, all solvent weld joints must be primed with purple primer visible at all joints.
    Same thing across the river in Jersey, need to use purple primer.

    Leave a comment:


  • geno gardner
    replied
    Re: I give up. whats wrong in this picture?

    Originally posted by SewerRatz View Post
    Trap arm dumping into a 45º and an improper island vent layout.
    Bingo.

    BTW: I added a little silicone spray to that Ro-Pump. Made all the difference. Now I don't have to use Arnold Shwartzeneger type strength to operate the thing. (good thing since I don't have that to begin with)

    Leave a comment:


  • Western Reserve
    replied
    Re: I give up. whats wrong in this picture?

    If this is, in fact, an island sink situation, where is that horizontal 1-1/2" piping going out through the cabinet?

    Leave a comment:


  • toolaholic
    replied
    Re: I give up. whats wrong in this picture?

    The Non Union CARPENTER knows. No sani tee

    Leave a comment:


  • Don the plumber
    replied
    Re: I give up. whats wrong in this picture?

    Here in Mich, that wye should be a tee. And if that 1-1/2" line coming up is a relief vent, or a revent, it should be tied into vent pipe above the flood level rim of sink, or fixture served, as code would say.
    Think about it, if that 1-1/2" line below the 1-1/2" wye clogs, the water could fill up to a certain level in sink, & then run into revent. Thats what i see anyway.
    Last edited by Don the plumber; 05-09-2010, 08:20 AM.

    Leave a comment:


  • Plumbfast
    replied
    Re: I give up. whats wrong in this picture?

    As an added note, at least in PA, all solvent weld joints must be primed with purple primer visible at all joints.

    Leave a comment:


  • jc60618
    replied
    Re: I give up. whats wrong in this picture?

    When the vent opening is at or below the level of the trap weir siphonage can occur. Therefore the vent opening must be at or above the trap weir. Thats the reason combos are not commonly use to pick up fixtures horizontal to vertical.
    Last edited by jc60618; 05-08-2010, 03:15 PM.

    Leave a comment:


  • SewerRatz
    replied
    Re: I give up. whats wrong in this picture?

    Originally posted by Aaron91 View Post
    Alright, someone posted this awhile back in strokefires thread, FrankenPlumbing. Is the fact that the trap arm goes into a 45 * before dumping into a wye what makes this ill legal or the trap adapter used in the horizontal application?
    Trap arm dumping into a 45º and an improper island vent layout.

    Leave a comment:


  • Aaron91
    started a topic I give up. whats wrong in this picture?

    I give up. whats wrong in this picture?

    Alright, someone posted this awhile back in strokefires thread, FrankenPlumbing. Is the fact that the trap arm goes into a 45 * before dumping into a wye what makes this ill legal or the trap adapter used in the horizontal application?
    Attached Files
    Last edited by Aaron91; 05-08-2010, 02:29 PM.