UPC W/M Code? Page Title Module
  • UPC W/M Code?
    Could someone list it? I won't be needing it for any reason. Just curious to learn what it currently says.
    Thanks.
    Re: UPC W/M Code?
    I give up. What's a W/M code????????????????
      Re: UPC W/M Code?
      Sorry. Washing Machine Code.
      The specific rules, dimension, & measurements associated with Washing Machine installations.
      Thanks.
        Re: UPC W/M Code?
        804.0 Indirect Waste Receptors.
        804.1 Plumbing fixtures or other receptors receiving the discharge
        of indirect waste pipes shall be approved for the use
        proposed and shall be of such shape and capacity as to prevent
        splashing or flooding and shall be located where they are
        readily accessible for inspection and cleaning. No standpipe
        receptor for any clothes washer shall extend more than thirty
        (30) inches (762 mm), or not less than eighteen (18) inches
        (457 mm) above its trap. No trap for any clothes washer
        standpipe receptor shall be installed below the floor, but shall
        be roughed in not less than six (6) inches (152 mm) and not
        more than eighteen (18) inches (457 mm) above the floor. No
        indirect waste receptor shall be installed in any toilet room,
        closet, cupboard, or storeroom, nor in any other portion of a
        building not in general use by the occupants thereof; except
        standpipes for clothes washers shall be permitted to be installed
        in toilet and bathroom areas when the clothes washer
        is installed in the same room.
          Re: UPC W/M Code?
          Interesting in that a trap is disallowed to be installed below the floor. I can see that on a slab as it makes it more difficult to access. But I can't see it for a crawlspace or basement where it would be the most accessible.
          I know the measurement requirements can also limit it though.
          Any requirement to upsize the pipe after the trap? We have to bump up to 3" here.
          Thanks.
            Re: UPC W/M Code?
            3" Trap and standpipe for a clothes washer JC?
              Re: UPC W/M Code?
              No. 2" Trap and Standpipe. Bump up to 3" after the trap outlet.
                Re: UPC W/M Code?
                If you have to use a fouling chamber there's something wrong with your install.
                  Re: UPC W/M Code?
                  My turn...What's a fouling chamber???????
                  Thanks.
                    Re: UPC W/M Code?
                    pretty sure a fouling chamber is the oversized pipe after the trap to allow for the wash water to back up a bit as it drains.
                    it isn't install specific, Nunya switched to requiring that a code book or two back
                      Re: UPC W/M Code?
                      Suds relief
                        Re: UPC W/M Code?
                        Originally posted by stokefire7 View Post
                        suds relief
                        urinal
                          Re: UPC W/M Code?
                          Well put.
                            Re: UPC W/M Code?
                            Checked my 06 UPC, looks like they did away with suds relief.
                              Re: UPC W/M Code?
                              Here's a good one.
