    Sizing for the individual job specs...it is important. One size does not fit all or most.
    Name:  7d89f7c45e2d0570a6aae3b63817ec30.jpg
Views: 1
Size:  4.8 KB
    AllurePlumbing.com
    • leak detection
    • drain cleaning
    • utility locating
    • conductor fault locating
    • and other specialties.

    Greensboro NC, Winston-Salem NC, High Point NC, Thomasville NC, Kernersville NC

  • #2
    Re: Gas Regulator Spring

    This is the wrong spring in a 5# gas regulator. The boiler only needed 6"wc at high fire. Since the boiler gas valve could handle 2psi someone installed a 1-3psi spring set to 2psi at high fire.
    AllurePlumbing.com
    • leak detection
    • drain cleaning
    • utility locating
    • conductor fault locating
    • and other specialties.

    Greensboro NC, Winston-Salem NC, High Point NC, Thomasville NC, Kernersville NC

    Comment


    • #3
      Re: Gas Regulator Spring

      What effect did it have on the burner flame? The owner should appreciate what you did.

      Comment


      • #4
        Re: Gas Regulator Spring

        Its on a Aerco Benchmark so seeing the flame is out. I walked by it and heard the thing hunting. They had electrical issues so they decided to change the gas spring...go figure. The gas valve wasn't hardly opening up 20% at high fire and would go off when it was at low fire. They over size the gas valve. They use 2" and can get by with 3/4".