RD8000 Generator Question

Page Title Module
Move Remove Collapse
X
Conversation Detail Module
Collapse
  • Filter
  • Time
  • Show
Clear All
new posts

  • RD8000 Generator Question

    I have a question that has stumped me and a few electricians that I asked, I even called up rigid tech support and they didn't know. The RD8000 has a capacity of 8000 watt running / 10000 watt starting, does the 30 amp plug have full access to this 8000/10000 capacity or is it limited to 7200 watts (30*240=7200)? The reason I asks is because I have seen some 8000 watt generators online that have 33.3 amp fuses (33.3*240 ~= 8000) but the RD8000 does not say what size fuses it has.

  • #2
    Re: RD8000 Generator Question

    http://www.ridgid.com/ASSETS/95FA20D...000-%20RPL.pdf

    The amperage draw through the 30 amp outlet is limited by the 30 amp Circuit breaker.

    Comment


    • #3
      Re: RD8000 Generator Question

      there is also a separate 120 volt 30 amp outlet and breaker along with the 120 volt 20 amp breaker.

      good job mark7 for posting the link and the facts.

      just wait, 2 electricians will be questioning the plumbers for posting the correct answer.

      rick.
      phoebe it is

      Comment


      • #4
        Re: RD8000 Generator Question

        Theoretically, your 7200 watts (30*240=7200) formula is correct.
        Theoretically, the 30 amp breaker on each of the 120 legs limits it to 7.2kw.
        In reality, though, I routinely run these units on a load bank dialed in to 8.5 - 9kw and have not yet had a breaker pop.
        "HONK if you've never seen a gun fired from a moving Harley"

        Comment


        • #5
          Re: RD8000 Generator Question

          I found the answer that you can pull up to 10 kw from the 30 amp plug for a short period of time to be true because the 30 amp breakers are thermal breakers which will not immediately trip

          I found the answer to be that you call pull all 10kw from this generator because it has thermal circuit breakers. A thermal circuit breaker will not immediately trip if you just go a little above its capacity. The 30 amp circuit breakers are a PE74 series whose spec sheet says you can run it at 135% for 1 hour before it trips.

          Spec sheet from the manufacturer is here:
          http://www.joemexcn.com/upfiles/2006060914235899319.pdf

          Comment